Gas fire-extinguishing control panel

LPCB certificate TC addressable fire alarm, conventional fire alarm, wireless fire alarm system manual download.
vedard
Posts: 911
Joined: Wed Dec 05, 2018 12:27 am

Gas fire-extinguishing control panel

Unread post by vedard »

JB-QB-QTC5015 control panel shall be installed wall-mounted, of which the typical configurations include: loop control part, loop part, direct control part, gas fire-extinguishing control part, power, etc. The system is a combination of alarm, linkage and gas fire-extinguishing. Control of fire alarm, common fire protection device start/abort and gas fire-extinguishing device can be realized through loop control panel or direct control panel.
JB-QB-QTC5015 Intelligent Fire Alarm Control Penal/Gas Fire-extinguishing Control Panel (short as Control Panel) is a new all-in-one generation of control panel combined of fire alarm linkage and gas fire-extinguishing control. The control panel also has linkage control function for construction designation need and the function to be compatible with other products to form up a fire alarm linkage integral control system, which is suitable for fire alarm and fire protection linkage integral control system. The control panel has the function of gas fire-extinguishing and can be applied for four zones. The control panel can be connected to emergency start/abort button, sounder strobe, gas spray indicator, auto/manual switch module and input/output module. With the function of networking, the control panel can also be connected to TC5000 series fire alarm control panel to form up a fire alarm and gas fire-extinguishing control.
gas extinguishing system wiring.JPG
gas extinguishing system wiring.JPG (92.5 KiB) Viewed 125850 times
Attachments
TC5015-Gas_Extinguishing_System_wiring.pdf
(172.16 KiB) Downloaded 5674 times
JB-QB-QTC5015 Gas Fire-extinguishing Control Panel Ver1.0.pdf
(6.24 MiB) Downloaded 4972 times
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 911
Joined: Wed Dec 05, 2018 12:27 am

TC5015 gas fire extinguishing controller isolation and release operation

Unread post by vedard »

When TC5015 gas fire extinguishing controller connected external equipment (detector, module or fire display panel) fails, it can be isolated, and after repair or replacement, the device can be restored by the release function.

TC5015 gas fire extinguishing controller isolation operation:

Press the "shield" key (if the controller is in the lock key state, you need to enter the user password to unlock), the screen display is as shown in the figure below. (Or enter the "User Settings" menu and then press "2" to enter the password to enter the "Device Shield" menu.)
1-1.png
1-1.png (144.94 KiB) Viewed 102434 times
Assuming that the equipment to be isolated is the photoelectric smoke detector of circuit 1, the isolation operation shall be carried out according to the following steps:

  ◇ Enter the loop and address of the equipment to be isolated;

  ◇ Press the "F1" key. If the device has not been isolated, the device will be added to the isolation information on the screen.

Unblock operation:

  press the "Unblock" key (if the controller is in the lock key state, you need to enter the user password to unlock), and the screen will display as shown in the figure below.
1-1.png
1-1.png (144.94 KiB) Viewed 102434 times
Assuming that the equipment to be de-isolated is the photoelectric smoke detector of circuit 1, the de-isolation operation shall be carried out according to the following steps:

  ◇ Input the loop and address of the isolation equipment to be canceled;

  ◇ Press the "F2" key, if the device has been isolated, the isolation information of this device will disappear on the screen.
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
Post Reply