How to cancel bypass zone or cancel zone of FC-7448

Home security system setting, operation troubleshooting. Help installing wireless wired home security system.
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

How to cancel bypass zone or cancel zone of FC-7448

Unread post by vedard »

FC-7448 is bus zone large capacity of burglar alarm, fire alarm control panel. 248 zones are available for monitoring and 2.4 km distance for communication.
If you have set bypass zone and now you want to cancel it. Then you should just repeat the bypass step again. That is press "bypass"+zone number again.
Below is the quick guide for programming FC-7448
1.Enter Programming mode by pressing 9876#0, (password +#0) then power LED and arm/disarm LED flash simultaneously, LCD display Prg:Mode4.05 Adr=
Exit Programming: Press “*” for 4s till “di” sound

2.Arm: press 1234(password) and “arm/disarm” button
3.Disarm: Press 1234(password) and “arm/disarm” button, LED of “arm/disarm” will be off
4.Force Arm: Press 1234(password) and “arm” + “bypass” buttons
5.Bypass: Press 1234(password) and “bypass”+xxx(zone No. with 3 digits)
6.Add user’s No. and password: press 1234#0, press “0”, then user No.(001-200), enter authority level(0-6) with “#”, then enter 4 digits password with “#”, password with “#” again.
7.Delete user id: Press 1234#0, press “0”, then user No.(001-200), enter user authority (0-6) with “#”, press 0#
8.Programming address:
0001-0030 is zone function program address
0031-0278 is zone program address
0415-0538 is zone features program address

9.How to fill in data:
The program address is 4 digits and value of address is 2 digits. After enter programming, LCD display Prog Mode 4.05 Adr= , Fill in “Adr=” with 4 digits program address. Then input 21#, then the two digits will be displayed alternately. Press “#”, it will display “1”, press “#” again, it will display “2”.(It is default and can be changed by programming), then skip to next program address. If you need to program some address, just press”*” twice and it will return to Prog Mode 4.05 Adr=
Note: FC-7448 is shipped from the factory as a working, pre-programmed control. Many of the programming address may already be set to the values you need. The default values are shown in Reverse Print. You don’t need to pre-program this address.

10.Program zone function (address is 0001—0030)
Zone function means the zone is delay zone, instant zone, 24 hours zone etc. It is already programmed into the panel but you can change the default and add new zone function according to user’s manual.

11.Zone programming (address is 0031—0278)
0031 means the first zone, 0032 is the second one and so on. If you want to set the eighth zone as 24 hours zone, then you need to change the value of this address to “07” and press # to confirm.
Note: This part is required to program according to requirement.

12.Cancel zone No.
Press 9876#0
Enter 0039(the ninth zone for example)
Enter 00# (the zone attribute will be cancelled)

13.Return to factory default
Press 9876#0
Enter 4058(return to default address)
Enter 01# to confirm

14. Alarm Telephone program and CID communication programming
Press 1234#0 to enter
Enter 9876#0
Enter 3159 (program address 3159, 3175, 3191 for 3 group alarm telephone)
Enter xxxxxxxxxxxxxxxx (max 16 digits telephone No.) with # to confirm

Determine Telecom Format
Press 9876#0
Enter 3157 (telecom format program address)
Enter 91 (Contact ID)

Program user’s code
Press 9876#0
Enter 3429
Enter 1230(user’s code is 123 for example, and need to add 0)

Alarm Report Programming
Press 9876#0
Enter 3153(program address)
Enter 11#

Program telephone dialing times
Press 9876#0
Enter 3154(program address)
Enter 12# (dial twice for example)

15.Control Panel time setting and arm/disarm timer program
Press 1234#0 + “2” to set date
Press 1234#0 + “6” to set time
Press 1234#0 + “1” to set auto arm time for every day
Press 1234#0 + “4” to set auto disarm time for every day


Remark: Please use 2.2K resistant for FC-7448 8 wired zones and use 47K resistant for expand module.
Authority grade is: 0 super user, 1 unlimited user, 2 combined user, 3 arm user 4 temporal user, 5 duress user, 6 entrance user
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

alarm system is not ready error showed when when arm/disarm

Unread post by vedard »

The alarm control panel can be armed/disarmed after programming finished. But after a while, it showed system is not ready and can not be armed/disarmed. Why?
After programming, the system will enter into self inspection process. At this time, fault may be not found, so, it can be armed /disarmed. But after inspection, fault is found and can not be armed, disarmed.
System is not ready, if no fault zone number is showed, then it is bus line error. Maybe short circuit of bus line exists.
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

Enroll infrared beam to FC-7448

Unread post by vedard »

Using address module FC-7401 to wire infrared beam to bus zone FC-7448. It showed zone is not ready but the beam transmission and receiver is aimed. What is wrong?
Change an address module to test. If problem still exists, then the beam is with problem.
How to find the problem of the beam sensor?
Power on the beams, calibrate the transmission and receiver terminals. Then use multimeter to test the two output signal terminals (3, 4), at N/C connection status, it should be short circuit. (0 ohm). Now, block the beam light using thick object between transmitter and receiver and test signal termial (3, 4) resistor again, it should be open circuit(∞ ohm)
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

How to connect FC-7448 with access control

Unread post by vedard »

Function: If the door is open, the access control will send switch signal to FC-7448, FC-7448 will dial out for voice alarm to preset phone number and CID security center.
Solution: Use FC-7448 address module to connect access control panel to FC-7448. So, the door open signal will send to FC-7448 and FC-7448 will send alarm information to security center via CID communication format. Add a 911 dialer to FC-7448 Bell out termial (12V output). Set Voltage input trigger for the 911 dialer.
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

FC-4010 can not communicate with PC

Unread post by vedard »

FC-4010 can not communicate with PC, why?
Please make sure the connection is correct. FC-4010 should be connected to the first group RBGY on the main board. Then make sure programming is right. It is 4019 18# then 4020 40#
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

How to connect FC-7448 with CCTV

Unread post by vedard »

Use FC-32 relay out module to connect FC-7448 with CCTV NVR and get image pop up when alarm occurs.
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

How to connect FC-7448 with programming keypad FC-7416

Unread post by vedard »

Connect FC-7416 to the second group of RBGY on main board (2nd group RBGY is for programming keypad)
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
vedard
Posts: 910
Joined: Wed Dec 05, 2018 12:27 am

Troubleshooting for FC-7448 bus-line alarm system

Unread post by vedard »

FC-7448 is professional grade commercial security system. It requires security service installation and maintenance.
There may be some malfunctions with the equipment during working period. How can we troubleshoot it? Below we list some common
malfunctions and help troubleshooting it.
1. The system showed "System fault"
Solution: Enter password "#87" to query. It showed system fault and no connection to backup battery. Correctly connect backup battery
to the alarm host and the trouble solved. If not need backup battery, the fault can be ignored and the security system can work normally.

2. FC-7448 showed "communication fault". There are some possible causes. a. The connection between the host and the keyboard is incorrect or bad.
b. The main keyboard is not correctly set with DIP switch, or the other keyboard is not programmed. 3. Hardware failure can also cause this problem.

3. FC-7448 showed "zone is not ready":Enter password "#87" to query. It showed zone fault. 1. Check corresponding zone module FC-7401 connection is good or not.
2. Check corresponding zone module FC-7401 DIP switch setting is correct or not. If not zone fault. 1. Check connection between zone module FC-7401 and detector is good or not.
2. Check whether or not the detector is triggering alarm cause intrusion detected in detection area.
3. Check the EOL resistor value is correct or not and connection is good or bad.
Shop Focus brand wireless alarm, HB solar power alarm, HST fire alarm at https://www.vedardalarm.com
Post Reply