Mini conventional fire alarm system

Posted: Tue Aug 18, 2020 10:19 am
by vedard
2 zones master and slave fire alarm control panel is microprocessor controlled and has 1 alarm sound output zones.(bell zone), a 24V supply energized on fire, one set of volt free changeover contacts which operate on fault, and two sets of volt free changeover contacts which operate on fire.
Conventional fire alarm system is suitable for small places
But for small place, such as hotel, villa, resident security, conventional fire alarm system is still suitable and convenient for installation and maintenance. Conventional fire alarm system is reliable as well and it is still used to control relay contact type device such as draught fan, water pump.
2-zone mini type conventional fire alarm control panel is very suitable for small business fire security. It has 2 zones and each zone can equip maximum 25 detectors. The panel has zone1 alarm, zone2 alarm and NAC alarm, zone1 fault, zone2 fault, NAC fault indication. Evacuate, silence, test/reset buttons can be operated on the panel. So, the fire security guard can easy understand the alarm information and operate the alarm panel to warn people of the fire event. Fire location can be easy found and fire extinguishing measure be taken cause the place is small. So, mini type conventional fire alarm system is very suitable for small business place such as hotel, villa, showroom, store. AC90-270V power supply with lead-acid backup battery and 1 alarm sound output zones (bell zones), which can equip max.16 sounders. The mini type fire alarm panel can expand to 4 zones, 6 zones etc. By adding slave alarm panel via RS485 connection.
Shop it at https://vedardalarm.com/fire-alarm-cont ... tion-p-115
Conventional detector is universal and can be used for any type conventional fire alarm control panel. There are smoke / heat /smoke &heat detectors or 4-wire smoke detector with relay output. The detector can be equipped with shutter door control box as well. When the detector alarms, the signal is fed back to the controller. The remote LED can be connected to the detector for clear view if the detector is installed in hidden place such as attic.
https://vedard.com/blog/conventional-fi ... all-places

Difference of conventional fire alarm and addressable fire alarm

Posted: Thu Dec 10, 2020 1:05 pm
by Jim
The difference is the connection mode of alarm circuit and power supply circuit of the equipment.
Multi-wire conventional fire alarm system
The (multi-wire) conventional fire alarm system refers to the detector (equipment) in each detection area, which is independent of the controller and has an independent signal loop. The signals in each detection area are input in parallel to the controller.
More details can be found at Vedard Security Alarm Technology

conventional fire alarm system manual

Posted: Sun Dec 13, 2020 2:32 pm
by Jim
This fire alarm control panel meets NFPA requirement. It should be installed, commissioned and maintained by suitably qualified service personnel.
Description:
1. It has 16 zones and 4 sounder outputs.
2. It has 3 standard FORM-A relays contact for alarm, fault, supervisory. And it has EIA-485 port for communication with remote delay and repeater panel.
3. It works with conventional N/O contact input devices including 2 wire, 4 wire smoke detector, heat detector, gas detector and call points etc.
4. It can be programmed by panel keypad. It is supervised all wiring, AC voltage and battery level.
5. It is required to be connected to power earth and it self checks earth fault.
6. Max.20 detectors can be equipped in one zone. Each zone can be disabled separately.
7. Output circuits:
24V resettable power output 1000mA
24V Nonresettable power output 1000mA
24V battery charger (up to 18AH battery)
8. EIA-485 port (interfaces to Annunciators, Graphic Annunciators and Remote Relay module)
9. 75VA power module is provided with the panel
10. Sound 1-4 output can be manual activate directly or disabled.
11. Panel running mode can be switched to manual or automatic.
12. It reports short and broken circuit of zones.
13. It is designed with space of 2 pcs sealed lead-acid backup battery.
14. It is with Test and disable function.
15. It can connect with Max.32 repeater panels by RS485 port.

Specification:
1. Power supply:AC90~270VAC 50Hz 3A
2. Wire size: Minimum #14 AWG (2.0mm²) with 600V insulation.
3. Detector loop current is sufficient to ensure operation of 2 alarmed detectors per zone. Standby current: 7.26mA
4. Three relay output
relay contact rating: 2A at 30VDC
5. Total DC current output: 500mA
6. Recommend Max. standby current: 150mA
7. Input circuits 1-16 zones may be used as standard fire alarm control panel zones and accpet N/O contact devices.
8. Output circuits
24V resettable power output 1000mA
24V Nonresettable power output 1000mA
24V battery charger (up to 18AH battery)
EIA-485 port
9. Dimension: 35cm*40cm*16.5cm
It is with space of 7AH backup battery
CK1000Manual.pdf
(3.92 MiB) Downloaded 2620 times

conventional 2-wire smoke detector

Posted: Sun Dec 13, 2020 3:11 pm
by Jim
Conventional Photoelectric Smoke Sensors
GENERAL DESCRIPTION
The device is photoelectronic detector uses a state of-the-art optical sensing chamber. This detector is designed to provide open area protection and to be used with most conventional fire alarm control panel.
Two LEDs on each detector provide local 360 visible alarm indication. They flash every 3~5 seconds indicating that power is applied and the detector is working properly.
The LEDs latch on in alarm. LEDs will be off when a trouble condition exists indicating that the detector sensitivity is outside the listed limit. The alarm can be reset only by a momentary power interruption.
IMPORTANT: The detector must be tested and maintained regularly following NFPA 72 requirements.
The detector should be cleaned at least once a year.
TAMPER-RESISTANCE
The detector include a tamper-resistant capability that prevents their removal from the bracket without the use of a tool.